Concerning a distribution power transformer (> 200 MVA) connected to the grid (220 kV), I am looking for similar failures in similar HV bushing connection transformers to try to compare with the type of failure we have had. And i'm not able to find information about transformers or failures in transformers with this type of connection.
The connection between the HV bushing and the HV cable is made in this way:
1) Oil to oil bushing
2) Link (short flexible cable between bushing and cable termination)
3) Cable termination
4) Oil Container (oil box?), independant for each HV phase, in which the previous elements are inmersed. Every oil container has an independant Buchholz protection and is breathing through the main conservator tank.
In the first energization of the transformer it was running properly for about two hours. A second connection activated temporarily one buchholz relay of the HV bushing containers(due to oil flow, not gas bubble). After checking buchholz and electrical protections, finding all them correct, the third energization generated an explosion in one of the HV bushing containers (one HV phase connection).
There was a ground failure between the end of the cable termination (cable supplier) and the oil container (transformer supplier). So we are trying to determine the potential cause and origin of the failure.
If you know an address or link where I can find connections and/or transformer failures of this type it would be helpful to me.
Thank you vey much in advance and kind regards.
The connection between the HV bushing and the HV cable is made in this way:
1) Oil to oil bushing
2) Link (short flexible cable between bushing and cable termination)
3) Cable termination
4) Oil Container (oil box?), independant for each HV phase, in which the previous elements are inmersed. Every oil container has an independant Buchholz protection and is breathing through the main conservator tank.
In the first energization of the transformer it was running properly for about two hours. A second connection activated temporarily one buchholz relay of the HV bushing containers(due to oil flow, not gas bubble). After checking buchholz and electrical protections, finding all them correct, the third energization generated an explosion in one of the HV bushing containers (one HV phase connection).
There was a ground failure between the end of the cable termination (cable supplier) and the oil container (transformer supplier). So we are trying to determine the potential cause and origin of the failure.
If you know an address or link where I can find connections and/or transformer failures of this type it would be helpful to me.
Thank you vey much in advance and kind regards.