bspace123
Electrical
- Sep 3, 2009
- 27
Hi all,
I'm trying to understand earthing requirements in a high/low voltage (6.6kV/0.4kV) installation. Can someone please clarify/confirm my understanding is correct based on some research I've done:
- For all high voltage equipment "conductive parts" (e.g. motor frames or terminal boxes) supplied with copper screened PVC insulated power cables, the copper screen is connected to the motor earthing terminal and acts as the protective earthing conductor for the motor. Obviously it is bonded to the earth system at the motor supply point. Is there an additional requirement to have a separate earthing conductor connected from the supply origin to the exposed parts?
- For all "extraneous parts" subject to EPR (e.g. metallic structures with underground concrete footings) they must be bonded to Earth. The earth conductor must be sized for the maximum available earth fault current, which may cause the EPR. Is there a requirement to bond these structures at two independent points ? (e.g. two individual bonding conductors connect the structure back to the earth grid)?
- For all extraneous parts not subject to EPR (e.g. metallic doors, removable metallic floor grating etc.), they must be bonded to Earth. I've been reading that this earthing conductor must be sized to half the size of the of the supply earth that the parts may be subjected to under fault conditions. For example, if temporary cables will be run through a door to supply test equipment, then the bonding conductor must be sized to at least half the size of the earth cable in those temporary cables (or 6mm2 for mechanical integrity), whichever is greater. Is there a requirement to bond these structures at two independent points?
Are there standards which specifically reference these scenarios and what the correct practice is?
I'm trying to understand earthing requirements in a high/low voltage (6.6kV/0.4kV) installation. Can someone please clarify/confirm my understanding is correct based on some research I've done:
- For all high voltage equipment "conductive parts" (e.g. motor frames or terminal boxes) supplied with copper screened PVC insulated power cables, the copper screen is connected to the motor earthing terminal and acts as the protective earthing conductor for the motor. Obviously it is bonded to the earth system at the motor supply point. Is there an additional requirement to have a separate earthing conductor connected from the supply origin to the exposed parts?
- For all "extraneous parts" subject to EPR (e.g. metallic structures with underground concrete footings) they must be bonded to Earth. The earth conductor must be sized for the maximum available earth fault current, which may cause the EPR. Is there a requirement to bond these structures at two independent points ? (e.g. two individual bonding conductors connect the structure back to the earth grid)?
- For all extraneous parts not subject to EPR (e.g. metallic doors, removable metallic floor grating etc.), they must be bonded to Earth. I've been reading that this earthing conductor must be sized to half the size of the of the supply earth that the parts may be subjected to under fault conditions. For example, if temporary cables will be run through a door to supply test equipment, then the bonding conductor must be sized to at least half the size of the earth cable in those temporary cables (or 6mm2 for mechanical integrity), whichever is greater. Is there a requirement to bond these structures at two independent points?
Are there standards which specifically reference these scenarios and what the correct practice is?