RRaghunath
Electrical
- Aug 19, 2002
- 1,729
The speed switch and prolongd start protection based on sped switch operation is recommended in cases where the starting time of the drive is greater than the thermal withstand time of the motor.
In one of clients' specifications, it is said that the hot withstand time at 110% rated voltage shall be greater by atleast 3seconds than the drive starting time at the lowest voltage of 80%.
To me, this appears overspecification and perusal of motor ratings reveals that if we apply the criteria as above all the motors would require to be provided with speed switch.
Solicit your opinion / experiences on the subject.
Just to clarify, I am only talking about pump drives.
Thanks in anticipation. Raghunath