Here are a few of my experiences....
1. Concrete-encased duct banks tend to work well in cycled loads with different circuits in them. We've been conservative in our cable loading limits, while exceeding them only for emergency conditions.
2. Conservative cable ratings has "saved us" in the past. 750 kcmil Al 15 kV cable has a rating of about 455 amps in conduit as a circuit by itself, and in a duct bank we'd limit it to about 350 amps. This is the 3-circuit rating of the cable. The 6-circuit rating is 280 amps. Direct buried this same cable in a trench by itself s good for 540 amps. This usually creates a buffer between what we think we know and what is actually there.
3. Sand tends to dry out quickly, but will also allow the inward migration of moisture afterwards. All of the really bad cable "cooks" I've seen have been in sand or sand-encased conduit. Here in Utah things can get pretty dry and hot in the summer, and without some source of moisture besides what little rain we get can be hard on sandy soil.
4. Some areas have used bentonite clay to help in retaining moisture around the cable. Clay is great for holding the moisture, but lousy in soaking it back up afterwards. I've heard of studies that other utilities have one that show several years for the soil to "heal" after severely overheating the soil for prolonged periods of time.
5. EPR cables can handle overloads a LOT better than XLPE cables. XLPE or TRXLPE goes through a phase change around 140 degrees C from a solid to a gellatinous material. When it does this it greatly expands. Concentric neutral cables will see the insulation be pushed out against the neutral wires. Tape shielded wires will see the tape split in half by the internal pressures being generated. EPR is a rubber, and when it overheats the plasticizers (the stuff that keeps the rubber flexible) are gradually drived out of the rubber. The cable will not fail at this point unless it is moved, and then the insulation is cracked. This happens at a temperature well above the melting point of the PVC jacket. Melting and damage to the cable jacket does not necessarily signify that the cable itself is damaged, at least in the case of EPR.
The cable that was in the very hot trench was 500 Cu TRXLPE 4kV cable with a tape shield. The conductor had sagged through the insulation part way, the insulation had swelled and split the tape shield, and the PVC jacket had hardened and cracked off.
Unless you have a very long run of cable to do, with very expensive cable, the "brute force" method may well be the most cost-effective method to use. Often there are just too many unknowns in the soil conditions along the route to be able to control what is happening.
How long is the cable run? How much current are you trying to carry between the two points? Is it all underground, or is some of it in overhead cable tray or such? I can give you my $0.02 worth of some suggestions if you want.
Mark in Utah