Oct 2, 2012 #1 cdafd Specifier/Regulator Aug 18, 2005 2,894 0 36 US does anyone have the wording out of NFPA 13 2013, they can post, that deals with the design if you have::: HVLS High Velocity Low Speed fans
does anyone have the wording out of NFPA 13 2013, they can post, that deals with the design if you have::: HVLS High Velocity Low Speed fans
Oct 2, 2012 Thread starter #2 cdafd Specifier/Regulator Aug 18, 2005 2,894 0 36 US found it not word for word 1. max 24 foot fan 2. centered between for sprinklers. 3. fan to be minimum 3 feet below sprinkler. 4. shut off upon water flow Upvote 0 Downvote
found it not word for word 1. max 24 foot fan 2. centered between for sprinklers. 3. fan to be minimum 3 feet below sprinkler. 4. shut off upon water flow
Oct 2, 2012 #3 LCREP Specifier/Regulator Feb 14, 2004 835 0 16 US CD, NFPA 13 2013 has not come out yet, should be in the next few weeks. **************************************** Fire Sprinklers Save Firefighters’ Lives Too! Upvote 0 Downvote
CD, NFPA 13 2013 has not come out yet, should be in the next few weeks. **************************************** Fire Sprinklers Save Firefighters’ Lives Too!