WBUW
Structural
- May 30, 2006
- 63
I'm new to using HydroCAD. I have the site modeled, I would like to include the pipe inside the trench for additional storage, but I'm having a hard time getting HydroCAD to do it.
I'm running version 8 so I already have all the downloads from the outer storage has been defined as a 4' wide by 4' deep by 99' long trench. I would like to include the perforated pipe volume in the storage calcs to see if I can reduce the length or depth of the trench.
I looked here for some reason the 'embed inside' box gives me no options other than 'nothing'.
Anyone have an idea what the problem could be?
Thanks,
Will
I'm running version 8 so I already have all the downloads from the outer storage has been defined as a 4' wide by 4' deep by 99' long trench. I would like to include the perforated pipe volume in the storage calcs to see if I can reduce the length or depth of the trench.
I looked here for some reason the 'embed inside' box gives me no options other than 'nothing'.
Anyone have an idea what the problem could be?
Thanks,
Will