Hi,
I am working in the area classification of a plant which involves some hydrogen pipes.
I am using the sources of release qualification method.
I have some formulas to calculate the horizontal extent of the zone. For example:
X = (920*Q/LEL)^0.55 (1)
Release from high level point source where X horizontal distance in meters, Q gas flowrate in m3/s and LEL lower explosive limit in vol %.
For a release from ground level there is a similar formula
X = (1849*Q/LEL)^0.55 (2)
Alternatively I am also using which calcultes the extent based on the degree of ventilation avalaible (ventilatin efficiency and number of air changes.
In the case of the a vent from a pipe placed outside both approaches reach a similar number.
My problem is that the the formulas 1&2 are not adequate for a emission which happens indoors and if I use the ventilation approach it results in number like a persistence time of 19 hours for a hypothetical leak of 0.16 g/h (leak through a 0.05 mm hole in a 1050 mbara line).
Sincerely I don't think that the hydrogen is going to take 19 hours for the hydrogen to dipserse.
It looks to me that these formulas are not applicable for the hydrogen case and its huge differencein density with the air.
I have been looking in some books I have from Dr. Frank Lees where he talks about dispersion models and I have found models for passive dispersion and for dense gas but nothing about light gases.
Does anyone know a formula applicable for calculation of distances for area classification in the hydrogen case indoors.
Thanks
I am working in the area classification of a plant which involves some hydrogen pipes.
I am using the sources of release qualification method.
I have some formulas to calculate the horizontal extent of the zone. For example:
X = (920*Q/LEL)^0.55 (1)
Release from high level point source where X horizontal distance in meters, Q gas flowrate in m3/s and LEL lower explosive limit in vol %.
For a release from ground level there is a similar formula
X = (1849*Q/LEL)^0.55 (2)
Alternatively I am also using which calcultes the extent based on the degree of ventilation avalaible (ventilatin efficiency and number of air changes.
In the case of the a vent from a pipe placed outside both approaches reach a similar number.
My problem is that the the formulas 1&2 are not adequate for a emission which happens indoors and if I use the ventilation approach it results in number like a persistence time of 19 hours for a hypothetical leak of 0.16 g/h (leak through a 0.05 mm hole in a 1050 mbara line).
Sincerely I don't think that the hydrogen is going to take 19 hours for the hydrogen to dipserse.
It looks to me that these formulas are not applicable for the hydrogen case and its huge differencein density with the air.
I have been looking in some books I have from Dr. Frank Lees where he talks about dispersion models and I have found models for passive dispersion and for dense gas but nothing about light gases.
Does anyone know a formula applicable for calculation of distances for area classification in the hydrogen case indoors.