The equation for calculating the time delay for NI type curve of any relay is
T = AD / ((I/Ipu )^B – 1)
And we know that for NI, we have A=0.14 and B= 0.02.
Suppose I am using this curve for any Electrical Load having FLA of 100A. Setting the pick-up at 120% of FLA, Ipick-up will be 120A.
From where i will get the value of "I"? I am doing the study on SKM, should I consider the Busbar 3P fault as "I" for all the loads connected to this switchgear or it shall be the SLG fault on that particular busbar or anything else. I am using SKM for the study. Let me know which value of “I” shall i choose.
T = AD / ((I/Ipu )^B – 1)
And we know that for NI, we have A=0.14 and B= 0.02.
Suppose I am using this curve for any Electrical Load having FLA of 100A. Setting the pick-up at 120% of FLA, Ipick-up will be 120A.
From where i will get the value of "I"? I am doing the study on SKM, should I consider the Busbar 3P fault as "I" for all the loads connected to this switchgear or it shall be the SLG fault on that particular busbar or anything else. I am using SKM for the study. Let me know which value of “I” shall i choose.