We need to do a quick running test. However the motor is
a 575V. We only have 460V. We've been told by the
motor supplier we could do this but to limit the run time
to 15 minutes to prevent over-heating.
The FLA are 226 @ 1.0 SF and its a 449TC Frame NEMA motor.
Should I set the motor for 226 as the nameplate reads or
less? Amps should go up with lower voltage so I'm hoping
there is enough motor to at least make duty.
Testing today let me know if there is anything I should
look for or expect. Nameplate speed is 1184 RPM I would
also suspect a lower speed with less voltage am I correct? Wayne E. Lovison