@ Mr. Parchie (Electrical)29 May 23 22:43
".....#1. There are lots of options. You can delete the use of the ELR, if your protection setup allows; .....#2. you can split your circuit so each branch leakage current cannot go over the ELR current sensitivity;.....#3... or you can replace those leaky devices with better ones. ....#4. Either way, the sensitivity of your ELR should be higher than your actual leakage current for smooth operations. .....#5. .. Remember, the length of your wire runs could add more leakage current seen by the ELR ".
I am of the opinion:
1. deleting it may not be allowed, otherwise the ELR would not have been there. In addition, it is not a good design without earth-fault protection, depending on over-current/short-circuit protection by MCB; which are at a much higher current value.
An alternative would be add a small time delay in the ELR say <0.4s to bridge the [accumulated] earth-fault current >250mA that may occur for [a short duration of say <0.3s].
2 to 4 are valid advice.
5. it was working fine before. There was no mention that the wiring being extended. However, it is valid that the [leakage current] increases with increase conductor length, but minimal.
Che Kuan Yau (Singapore)