I have the following that ended up in a building.
Two redundant biosafety level 3 (BL-3) exhaust fans are served by a variable frequency drive (VFD). The VFD is equipped with a disconnect and a hand-off-auto switch, configured for interaction with the building automation system that will allow indication for the operators, lead-standby, etc.
Trouble is, the VFD is supplied by a panel at the motor control center that is equipped with overload, another disconnect, and another hand-off-auto switch. The 'auto' position I believe allows for BAS control, but the BAS control will occur at the VFD. So what will the auto switch position at the MCC do?
I recommended to replace the MCC control with a simple disconnect, so that the VFD will serve the H-O-A control and BAS interface. The owner has decided that the current config may be acceptable, so long as it works. I hate to be negative, but I think this installation is poor practice for a BL-3 application. I have more of a mechanical & HVAC background, and I think of it like a VAV box inline with a VAV box, or two flow control functions in series. Not to mention another location from which the fans can be shutdown by accident. Do you have an opinion on this?? Thank you, -CB
Two redundant biosafety level 3 (BL-3) exhaust fans are served by a variable frequency drive (VFD). The VFD is equipped with a disconnect and a hand-off-auto switch, configured for interaction with the building automation system that will allow indication for the operators, lead-standby, etc.
Trouble is, the VFD is supplied by a panel at the motor control center that is equipped with overload, another disconnect, and another hand-off-auto switch. The 'auto' position I believe allows for BAS control, but the BAS control will occur at the VFD. So what will the auto switch position at the MCC do?
I recommended to replace the MCC control with a simple disconnect, so that the VFD will serve the H-O-A control and BAS interface. The owner has decided that the current config may be acceptable, so long as it works. I hate to be negative, but I think this installation is poor practice for a BL-3 application. I have more of a mechanical & HVAC background, and I think of it like a VAV box inline with a VAV box, or two flow control functions in series. Not to mention another location from which the fans can be shutdown by accident. Do you have an opinion on this?? Thank you, -CB