jeffhed
Structural
- Mar 23, 2007
- 286
Our firm is looking at a small addition to an existing tilt up building. The original building is 12,676 sq. ft. with a reentrant corner. The addition will fill in the reentrant corner and is 1,224 sq. ft. No exsiting walls will be altered in any way so the only concern is the increase of load to the existing building. My question is this 3403.2 states that no force imposed on the existing structure may be more than a 5% increase. Then 3403.2.3 states that smic load increase must be less than the 10% allowed by 3403.2.3. Both of these items trigger a reanalysis of the structure elements that are experiencing additional loads. 3403.2.3 aslo has 3 exceptions for addition not stand alone that will not trigger a reanalysis. Seismic loads will not be increased by more than 10% but the gravity load for one wall will increase more than 5%. Do I still need to reanalyze the wall even though it falls under the exceptions for seismic? The reason I am asking is because the structure is old with no construction docs to be found. We are trying to find a way besides designing the addition as completely stand alone to avoid reanalyzing the walls due to absence of documents on the project. Any ideas?