- Dec 13, 2000
- 2,306
I have a 2 story building that has eccentrically braced frames through entire length at each story. The frames are stacked. This is seismic category C. I will design the collectors at the roof for the special combinations of 1605.4.
I'm not sure what to do for the second floor collectors. The roof forces will be going directly into the 2nd flr frames from the columns, plus the collectors have to be designed for the 2nd floor seismic force too. But how should this total horiz. load to the 2nd flr collectors be combined (Qe)?
1) Omega x[roof minimum + floor minimum diaph force]
Minimum meaning comparing EQ.16-41 to EQ.16-64 for each
level, using the one that controls in each case.
2) Omega x[floor minimum diaphragm force (16-41 or 16-64)
+ the roof level force from 16-41].
3) Omega x[floor minimum diaphragm force only] + roof force
from 16-41
I'm not sure what to do for the second floor collectors. The roof forces will be going directly into the 2nd flr frames from the columns, plus the collectors have to be designed for the 2nd floor seismic force too. But how should this total horiz. load to the 2nd flr collectors be combined (Qe)?
1) Omega x[roof minimum + floor minimum diaph force]
Minimum meaning comparing EQ.16-41 to EQ.16-64 for each
level, using the one that controls in each case.
2) Omega x[floor minimum diaphragm force (16-41 or 16-64)
+ the roof level force from 16-41].
3) Omega x[floor minimum diaphragm force only] + roof force
from 16-41