JAE
Structural
- Jun 27, 2000
- 15,463
We have a project within our city where the IBC 2000 is adopted. On our plans, we indicated which special inspections were required per chapter 17. The plans call for the contractor to coordinate with the special inspector (i.e. notify the S.I. when work will begin so special inspections can be performed).
We just received a report from the project manager (an independent firm hired by the owner to oversee their projects....i.e. the owner's agent). The report is from the special inspection firm who completed the form last May on concrete masonry walls.
These are CMU walls that are load bearing, and also serve as shear walls for the structure. They are reinforced and grouted in spaced cells.
The report shows that all the "periodic" inspections were completed but that full time (continuous) inspections were not provided for grouting. In fact, the report states that they arrived at the site and some of the walls were already grouted. It goes on to say that the contractor was wet-stabbing bars into the grout so they checked "NO" on the boxes dealing with lap splices and inspection of rebar before grouting.
Now the project manager is asking us to comment/review the report (which we did not get in May). My question is:
What can be done at this point to ensure the wall is "acceptable"? The CMU walls are all completely enclosed by exterior veneer and interior finishes. The inspections indicated a questionable practice of wet-stabbing and now we as EOR have to comment on this.
The IBC has no apparent provisions for responding to missed inspections. Suggestions?
We just received a report from the project manager (an independent firm hired by the owner to oversee their projects....i.e. the owner's agent). The report is from the special inspection firm who completed the form last May on concrete masonry walls.
These are CMU walls that are load bearing, and also serve as shear walls for the structure. They are reinforced and grouted in spaced cells.
The report shows that all the "periodic" inspections were completed but that full time (continuous) inspections were not provided for grouting. In fact, the report states that they arrived at the site and some of the walls were already grouted. It goes on to say that the contractor was wet-stabbing bars into the grout so they checked "NO" on the boxes dealing with lap splices and inspection of rebar before grouting.
Now the project manager is asking us to comment/review the report (which we did not get in May). My question is:
What can be done at this point to ensure the wall is "acceptable"? The CMU walls are all completely enclosed by exterior veneer and interior finishes. The inspections indicated a questionable practice of wet-stabbing and now we as EOR have to comment on this.
The IBC has no apparent provisions for responding to missed inspections. Suggestions?