i. For cantilever members, l shall be taken as twice the length of the cantilever.


Any experienced man can explain that note ????????
 
Replies continue below

Recommended for you

The deflection limits are usually based upon the amount of curvature in the beam - this goes back to when a lot of buildings had lath and plaster ceilings.

Too much curvature can distress the connections between the plaster and structure - or crack the plaster due ot the lengthening along the curve.

Since the limits for the curvature are simplified to be based upon the deflection as a percent of length (L/360 for example) this is based on simple span beam deflection vs. curvature.
A cantilever in deflection can be envisioned as a half length of a simple span beam. Thus, to equate the L/360 deflection limit you would use 2 x L(cant) to get an equivalent simple span beam length.