dhoward26
Structural
- Jun 2, 2011
- 160
I'm starting to get a little more into ICF designs for custom homes and have some questions about columns and jambs.
For openings, where in the ACI code does it talk about when you need to provide ties and when you don't? ACI318-11 Section 7.10.5.1 states that "All nonprestressed bars shall be enclosed by transverse ties" when talking about compression members. What are the limits as to when you do or don't need to provide ties? And for Jambs, should I provide the minimum tie spacing required for all Jambs? Most loads on the jambs aren't more than a few thousand pounds.
I don't plan on using the waffle system of the ICF's to support larger point loads. I have some point loads from Girder Trusses that are around 5,000 lbs and it just doesn't seam too logical to provide a tied column under this when it is coming down on a wall and no opening. I will direct the contractor to provide a vertical bar underneath of it though. The wall systems are generally laid out such that my columns aren't part of the main lateral force resisting system. They support vertical loads and out-of-plane lateral loads from the openings only...except very special cases.
For openings, where in the ACI code does it talk about when you need to provide ties and when you don't? ACI318-11 Section 7.10.5.1 states that "All nonprestressed bars shall be enclosed by transverse ties" when talking about compression members. What are the limits as to when you do or don't need to provide ties? And for Jambs, should I provide the minimum tie spacing required for all Jambs? Most loads on the jambs aren't more than a few thousand pounds.
I don't plan on using the waffle system of the ICF's to support larger point loads. I have some point loads from Girder Trusses that are around 5,000 lbs and it just doesn't seam too logical to provide a tied column under this when it is coming down on a wall and no opening. I will direct the contractor to provide a vertical bar underneath of it though. The wall systems are generally laid out such that my columns aren't part of the main lateral force resisting system. They support vertical loads and out-of-plane lateral loads from the openings only...except very special cases.