Not enough information. Could be too small a VFD for the motor and load, could be an overly restrictive trip setting in the configuration, could be a defective motor, or a defective drive.
Incoming phase loss is a usual suspect for that. Also, extreme line notching can do it. If there are other large converters on the same transformer, such as large DC drives, that can be the result.