Identifying Load Bearing Wall? 1

Status
Not open for further replies.

Redacted

Structural
Mar 12, 2016
160
Hi there,

A client recently reached out to me with regard to a load bearing wall. Another structural engineer originally specified that the wall be demolished and replaced with a steel beam as it was assumed the existing wall was load bearing.

However, the client said that the contractor demolished the wall and during this process found that there was a gap between the floor joists and top of wall of about 2” (joists were not resting on the wall).

Site photo is shown below :

Screenshot_20220717-233008_Gallery_-_Copy_nloh9q.jpg


The client reached out to the original EoR, however, he appears to have left the country and is not answering emails, so they reached out to me to look at the wall instead. They want a report written to confirm whether the steel beam to replace the demoed wall is still required.

If the wall is not load bearing, the floor joists would span between the existing beam and adjacent wall. See below sketch showing the assumed joist span in green and the cmu wall that was demolished in hatched red.

Floor_Joist_-_Copy_mlgroy.png


I want to make sure that I am checking all my bases here. So a few things to note/ask :

1. The north beam that the floor joist is bearing on, shown in the sketch above is hidden inside of a drywall bulk head, so I’ll get the contractor to cut a hole so that I can confirm that there is a beam there and that the joists are resting on it. I already saw that the joists were resting on the farthest south wall.

2. Although the contractor and client are claiming that the joists were not resting on the demolished wall. I didn’t see this, as when they called me on site the wall was already demolished. I’ll ask to see if they took photographs of the gap above the wall but what else can be done to verify the claim?

3. I guess if nothing is provided I can measure the cross sections of the floor joists and attempt to determine if the span without the intermediate support (demoed wall) is appropriate, although the floor loading criteria/requirements is unknown.

4. Are there any other considerations I should be making for this?
 
Replies continue below

Recommended for you

I would definitely run a check on the joists or at least compare with the allowables in IBC. Consider delection especially, You don't want these owners to come back asking why their floor feels bouncy even if this change didn't cause it they could look to you as the last guy that touched it.

Other thing to consider is whether the wall was a shear wall. Most likely not in this case cause I don't see any blocking in the floor.

Could look for any joist splices or other discontinuites that would help you understand what is going on there.

Could also consider looking for a footing but that's probably a lot of work.





 
First, make sure right above that wall you just removed, there is no load bearing wall above. Figure out the joists and see how much it can span. What do you mean the floor loading criteria is not known?

The fact that the joists dont stop and start there, and the fact it doesnt have blocking between joists, more than likely it is not load bearing wall. But you still need to double check. Even if it wasn't a load bearing wall, it was still holding load. You never know with these old construction. Sometimes you remove a non load bearing wall but drywall starts to crack because it was "supporting" the floor above and the wall sits on the middle of joists below.
 
For me it has the look of an non load bearing wall, however without clear photos that the contractor took, you can't be sure and unless you really really trust the contractor then you must assume that it was actually supporting the beams. The fact the ceiling structure (plasterboard?) stops and starts at the wall shows the wall went in first and hence the suspicion is that it was supporting the joists.

You absolutely though need to know what is above it. Someone could easily have looked at the wall below and used that as a supporting wall and built something on top or loaded the floor appropriately.

that single picture isn't very high quality and which way is it looking? The drawing shows two doors?

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
 
Also the contractor is not very good. I mean they shore up the floor with flat 2x lol.
 