Umtully1
Electrical
- May 23, 2012
- 9
I've got a question regarding IEC 60909. Can someone explain how the different fault levels, ip, I"k, and Ik relate to different pieces of equipment. Specifically in relation to MCC, variable frequency drives and transformers?
I've gone through the standard and understand how those three numbers are calculated, but I don't recall ever once seeing how to apply them to equipment specifications.
For example, at a 2.5MVA transformer, according to etap we have I"k=33kA, IK=30kA, and iP=82kA. Now a hand calc, given the voltages and impedance of the transformer tells me that the maximum fault current that should be able to go through the transformer is about 35kA (690V, 6%Z). So how is it that iP = 82kA? The fault current through the transformer will automatically be limited by the impedance to 35kA right? There's no motor contributions on the secondary.
Am I missing something?
Scott
I've gone through the standard and understand how those three numbers are calculated, but I don't recall ever once seeing how to apply them to equipment specifications.
For example, at a 2.5MVA transformer, according to etap we have I"k=33kA, IK=30kA, and iP=82kA. Now a hand calc, given the voltages and impedance of the transformer tells me that the maximum fault current that should be able to go through the transformer is about 35kA (690V, 6%Z). So how is it that iP = 82kA? The fault current through the transformer will automatically be limited by the impedance to 35kA right? There's no motor contributions on the secondary.
Am I missing something?
Scott