Can i get details for IEC 61850 standard is working for High impedance Restricted earth fault prot. scheme for Transformers?
 
Replies continue below

Recommended for you

Hi 00123456 .
IEC61850 standard not declarated any protection functionality ( only names of function, communication protocols , etc).
For REF detalies please see in the forum date 14.11.2000,
sorry Im new here and don't know do links. You have greate explanation for REF
 
Slavagar is right. The standard has nothing to do with the application, in principle. It describes which signals (logical attributes etc... but they are actually "signals") the logical nodes (function) should at least have and how they should be called (so, how the protection is mapped in the standard).
 
Hi slavagar,

Just under the thread title in large blue text is the thread number in smaller blue text. For example the number of this thread it is [ignore]thread238-185060[/ignore]. If you cut and paste that number into your post the site will automatically create the link for you as it has in this reply (it also appends the title automatically).