IEC LV MCCB Trip Curves

Status
Not open for further replies.

Modula2

Electrical
Aug 3, 2002
81
I am trying to understand and interpret tripping curves presented by IEC LV MCCB manufacturers, specifically thermal magnetic. These are normally presented as single curves. There must be non-tripping time and current-breaking time with tolerances. For US devices, we usually see the min/max or open/close curves presented, which is useful for coordination/selectivity and for life safty evaluations such as arc flash hazard. Can someone point me in the right direction.
 
Replies continue below

Recommended for you

For IEC MCCBs see IEC MCCBs specifications including +/- current and time tolerances are in Standard IEC 60947-2.
eg. Longtime pickup current is between 1.05 to 1.20 x In.
Magnetic (Inst) pickup tolerance is -0.80 / +1.20 x In.
The IEC Standard describes Catergory A MCCB as MCCBs with no intended time-delay for the Short-Time pickup element.
Category B MCCBs have usually adjustable Short-Time Time delays to assist in grading with downstream MCCBs.
The Standard also refers to 'current limiting MCCBs' which can achieve grading between Category A MCCBs provding the let-thru I2t of the downstream MCCB is less than the I2t unlatching I2t of the upstream MCCB. This can only be determined from certified manufacturer look- up tables.
ie. the upstream and downstream MCCBs must be from the same manufacturer.
Hope this helps.
Murray Newman
 