Dear All,
Have anyone experienced the problem in comparison between the calculated Idc system short-circuit current and circuit breaker rating using IEC standard ?
I have one small power plant project which the owner had bought several small generators size from 8MVA to 17MVA and connected to the same system bus at 6.6kV voltage. The system is connected with utility grid through 69/6.9kV 25MVA transformer with high X/R at 45.49 as they want to have low loss. The result is that the DC component short-circuit current is very high.
I studied short-circuit current using ETAP6.0, the result shows that the Ib sym, Ib asym, Ip are within CB rating but very near its rating.
However Idc of short-circuit current exceed the Idc rating of CB approx. 4kA.
The CB used are the standard IEC CB having time constant 45ms, 50kA rated short-circuit breaking, 1 sec.Type ABB VD4.
Consultant said that the CB have not enough rating for Idc breaking even all other including Ib asym are within CB rating limit due to IEC requires all these four parameters be compared in considering the sufficiency of short-circuit breaking.
However there is the clause Annex-I section I.2.1 c)in IEC 62271-100 which seems to mean that " in case of Idc exceed breaker DC rating limit but the Ib asym is still lower than CB asymmetrical breaking rating, then this IEC deems as the CB have sufficient short-circuit rating for this application and Idc is not required to be considered ".
Is this understanding is correct ?
Could you please advise.
Thank you very much.
Have anyone experienced the problem in comparison between the calculated Idc system short-circuit current and circuit breaker rating using IEC standard ?
I have one small power plant project which the owner had bought several small generators size from 8MVA to 17MVA and connected to the same system bus at 6.6kV voltage. The system is connected with utility grid through 69/6.9kV 25MVA transformer with high X/R at 45.49 as they want to have low loss. The result is that the DC component short-circuit current is very high.
I studied short-circuit current using ETAP6.0, the result shows that the Ib sym, Ib asym, Ip are within CB rating but very near its rating.
However Idc of short-circuit current exceed the Idc rating of CB approx. 4kA.
The CB used are the standard IEC CB having time constant 45ms, 50kA rated short-circuit breaking, 1 sec.Type ABB VD4.
Consultant said that the CB have not enough rating for Idc breaking even all other including Ib asym are within CB rating limit due to IEC requires all these four parameters be compared in considering the sufficiency of short-circuit breaking.
However there is the clause Annex-I section I.2.1 c)in IEC 62271-100 which seems to mean that " in case of Idc exceed breaker DC rating limit but the Ib asym is still lower than CB asymmetrical breaking rating, then this IEC deems as the CB have sufficient short-circuit rating for this application and Idc is not required to be considered ".
Is this understanding is correct ?
Could you please advise.