Codemaster
Electrical
- Sep 1, 2002
- 13
I would like to install a 480V, 3ph, 60A, 40hp rated IEC receptacle on the load side of a 100A CB, IEC 60A contactor, and 23-75A adjustable electronic overload for a 30hp motor. I have used receptacles many times to feed portable motor loads that have a portable motor starter on them, but this is the first time that the motor starter is fixed and the motor is portable. I didn't see anything in the NEC that specifically prohibited this practice. My concern is that someone could accidently plug in a non-motor load or even a smaller portable motor. The overloads set at 40A for a 30hp motor would trip faster than a 60A circuit breaker would, but of course it still might not meet NEC. I am not certain if 1999 210-21(b)(1) or Table 210-24 applies in this circumstance. I don't see much is 430 regarding receptacles. Any comments?