EddyWirbelstrom
Electrical
- Feb 17, 2002
- 214
SKM’s PTW Arc Flash IEEE 1584-2018 calculates additional:
- “Flash Boundaries” based on user defined incident energy, and
- “Incident Energy” based on user defined additional Working Distances.
As shown in attached file,my manual calculations agree with the PTW32 Ver 9003 results 2), 3), and 4) in Fig. 1.
However the PTW results 11) and 12) in Fig. 1 are incorrect.
Figure 1 - SKM PTW IEEE1584-2018 Results
Can someone validate my calculations which show:
- 11) AF_FB@IE1 = 2524 mm, at 1.2 Cal/cm2
- 12) AF_FB@IE2 = 610 mm, at 11.62 Cal/cm2
Can someone validate my calculations for 11) and 12) using a IEEE 1584-2018 spreadsheet ?
The correct results for 2), 3), 4) contradict the incorrect results for 11) and 12).
- “Flash Boundaries” based on user defined incident energy, and
- “Incident Energy” based on user defined additional Working Distances.
As shown in attached file,my manual calculations agree with the PTW32 Ver 9003 results 2), 3), and 4) in Fig. 1.
However the PTW results 11) and 12) in Fig. 1 are incorrect.
Figure 1 - SKM PTW IEEE1584-2018 Results
Can someone validate my calculations which show:
- 11) AF_FB@IE1 = 2524 mm, at 1.2 Cal/cm2
- 12) AF_FB@IE2 = 610 mm, at 11.62 Cal/cm2
Can someone validate my calculations for 11) and 12) using a IEEE 1584-2018 spreadsheet ?
The correct results for 2), 3), 4) contradict the incorrect results for 11) and 12).