IEEE 43-2000

Status
Not open for further replies.

sngpl

Electrical
Feb 7, 2002
54
IEEE standard 43-2000 states that in order to avoid the effects of temperature in trend analysis, all tests should be corrected to a common base temperature of 40 degrees C using the following equation:

Rc = Kt * Rt

Where:

Rc is the insulation resistance corrected to 40 C
Kt is the insulation resistance temperature coefficient at t degrees C.
Rt is the measured insulation resistance (Mohm) at t degrees C.

My question is :

How do we know the value of Kt for a particular generator? I know we can calculate it by making measurements at several temperature and plotting the results on a semi logarithmic scale but I am afraid we have missed this opportunity as all of our generators are on bar at full load, being the peak flow season.

Any help shall be highly appreciated.
Thanks
 
Replies continue below

Recommended for you

I finally found the answer to my question:

Kt= (0.5)^ ((40-t)/10))

where t is the actual insualtion temperature.

Thanks anyway!!
 