I have an application where I want to add concrete encased ground rods on the perimeter of my plant to reduce the copmbined ground resistance. The resistivity around the ground mat or grid conductors is high about 500ohm-m. The resistivity of the concrete encased electrodes will be assumed around 20ohm -m. So my ground rods now become 70ohms instead of around 300ohms.
My question is : for the combined resistance in which I use to determine the GPR, I need to use a resistivity for the mutual ground resistance between the ground grid and rod bed. Do I use something between 500ohm-m and 20ohm -m ?
or is this not possible due to the inherent capibility of the formula. The total grid area is about 16,000m2. The concrete foundation cannot be used because it is "insulated" by a vinyl liner under the entire area which can't be punctured.
In other words the resistivity I use in the Schwarz equations will be a estimated value between the ground resistivity and the concrete rod resistivity?
Thanks
My question is : for the combined resistance in which I use to determine the GPR, I need to use a resistivity for the mutual ground resistance between the ground grid and rod bed. Do I use something between 500ohm-m and 20ohm -m ?
or is this not possible due to the inherent capibility of the formula. The total grid area is about 16,000m2. The concrete foundation cannot be used because it is "insulated" by a vinyl liner under the entire area which can't be punctured.
In other words the resistivity I use in the Schwarz equations will be a estimated value between the ground resistivity and the concrete rod resistivity?