IEEE C57.12; Transformer Fault Testing

Status
Not open for further replies.

fluxcap

Electrical
Dec 4, 2003
9
US
IEEE C57.12 includes single phase to ground, two phase to ground and three phase faults as withstand tests/design criteria for liquid filled transformers.

Is it logical to assume that a transformer should withstand a three phase TO GROUND thru fault on the secondary as well. This is sometimes (and perhaps too often) applied when a system is energized into a set of safety grounds or a grounded three phase switch.

This is assuming that the transformer protection is set properly to clear within the damage curve timing(durations of 2 sec for cat II, III, IV of the C57 spec).

I have reviewed the positive and zero sequence models and can see no (electrical) theoretical difference between the three phase to ground and a straight three phase fault (on the wye secondary system). Anything going on electro-mechanically that I am neglecting? or should we expect a transformer to hold up to this type of thru fault?

Thanks in advance.
 
Replies continue below

Recommended for you

If all poles close simultaneously there is no difference. In reality, pole closures are somewhat staggered, so the fault evolves from SLG to DLG to 3phase.
 