JensenDrive
Electrical
- May 25, 2007
- 120
At the end of chapter 4 of the 1993 IEEE Red Book (Std 141) there are some typical cable impedances (the 1986 version does not seem to have the tables). For a given AWG or kcmil, the tables give the same reactance for 600V and 5kV nonshielded cablereactance, XL. I know the tables is a rough/typical estimate because how cable is lain in the tray/conduit/trench has a large effect on reactance, but still, I am a bit surprised that the two voltage levels have about the same reactance, per the tables. I do not deal with 5kV cable in my line of work, but I would expect it to have thicker insulation than 600V cable. Thicker insulation means larger wire-wire spacing, which will cause higher XL, so you can guess that I am scratching my head; "How can these two voltage classes have (roughly, of course) the same XL for the same AWG?" Two answers come to mind:
a) Maybe 5kV non-shielded insulation is higher grade but not really much thicker compared to the insulation used at 600V.
b) Maybe how the cables are placed in the conduit/trench/tray has a such a huge effect on spacing, relative to insulation thickness, that there is not much point in different tables for the two voltage classes.
Questions for the group:
1) Do either of these answers make sense?
2) Any other explanations come to mind?
3) If cable reactances actually are a little different for the two cable voltage levels, do the tables more closely represent 600V or 5kV cables?
4) Do you feel comfortable using these Red Book impedances in fault and voltage drop calculations?
a) Maybe 5kV non-shielded insulation is higher grade but not really much thicker compared to the insulation used at 600V.
b) Maybe how the cables are placed in the conduit/trench/tray has a such a huge effect on spacing, relative to insulation thickness, that there is not much point in different tables for the two voltage classes.
Questions for the group:
1) Do either of these answers make sense?
2) Any other explanations come to mind?
3) If cable reactances actually are a little different for the two cable voltage levels, do the tables more closely represent 600V or 5kV cables?
4) Do you feel comfortable using these Red Book impedances in fault and voltage drop calculations?