On a project long,long ago in a state far, far away, we once installed 2 bonding autoclaves, each with a 3 MW 480VAC electric heater. Each heater had 5 3-phase circuits, power was controlled by zero-crossover SCR (thyristors) on 2 of the phases, the third phase being directly wired. When the thyristors were switching, there was an obvious flicker of the plant lighting, which we thought might be a problem. There was a nearby town where a small hydroelectric generation station was located. Once the system was put into production and operation continued into the night, it didn't take long before we realized that the street lights in town flickered also. The electric supply to the plant was 69 KV, stepped down to 12470 which fed 2 double ended substations. So the transients were getting all the way to back to the grid. We were thus faced with the option to replace 10 zero-crossover SCRs with phase-angle type(big bucks), or to find another solution. We found a device that allowed the zero crossover SCRs to function like solid-state contactors, using time-proportional on/off control, and it also staged the outputs so that each SCR would share an equal duty cycle. This saved the day, at least as far as THAT issue was concerned.