- Dec 28, 2019
- 4
I am working on a short circuit calculation for three 3ph 75kVA transformers in parallel. All three are identical with 1.9%Z.
The total bank rating is then 3x75kva = 225kVA. But I'm not sure on the equivalent impedance? Would it be 1/ZT = 1/z1 + 1/z2 + 1/z3 (Where z1/2/3 all equal 1.9%) which would give an equivalent of a 3ph 225kVA transformer with Z=0.6333%?
If the transformers were three 1ph all with 1.9%Z, then as I understand it the total equivalent would also be a single 3ph 75kVA with Z=1.9% correct?
Thank you!
These are my numbers so far below... but I'm not sure on the Z which effects everything else downstream.
--------------------------------------------------------------------------------
Line-to-Line (L-L) Fault
Fault X/1
I/FL =
=3 x 75kVA x 1000 = 216.51 A
600 x 1.732
Multiplier =
= 100
1.9% x 0.9*
= 58.48
The total bank rating is then 3x75kva = 225kVA. But I'm not sure on the equivalent impedance? Would it be 1/ZT = 1/z1 + 1/z2 + 1/z3 (Where z1/2/3 all equal 1.9%) which would give an equivalent of a 3ph 225kVA transformer with Z=0.6333%?
If the transformers were three 1ph all with 1.9%Z, then as I understand it the total equivalent would also be a single 3ph 75kVA with Z=1.9% correct?
Thank you!
These are my numbers so far below... but I'm not sure on the Z which effects everything else downstream.
--------------------------------------------------------------------------------
Line-to-Line (L-L) Fault
Fault X/1
I/FL =
=3 x 75kVA x 1000 = 216.51 A
600 x 1.732
Multiplier =
= 100
1.9% x 0.9*
= 58.48