For a ground fault or single-phase-to-ground fault, the symmetrical component solution is a series connection of Z1, Z2 and Z0. The resulting current, I1, will be obtained from V/(Z1+Z2+Z0). For the actual fault current, If, you need to multiply I1 by 3.