In rush current

Status
Not open for further replies.

Guardiano

Electrical
Nov 11, 2008
118
Hi,
I am actually setting my protection relay on a 7.5MVA 22/11 kV transformer and would like to know if 12 times rated current is a safe setting for the inrush current.
Thanks.
Guardiano
 
Replies continue below

Recommended for you

Yes.It is a safe setting. Inrush can be 8-12 times full load current for this range of transformers,
 