Incoming device as Disconnector Switch / Isolator

NickParker

Electrical
Sep 1, 2017
403
See the picture below, Can the incoming device be a disconnector switch or a circuit breaker?
I am looking for both IEC and NEC codes that permit the use of disconnector switches as incomers.

Disconnector switch.JPG
 
Replies continue below

Recommended for you

The device must be rated for the application.
For instance, if the example is ruled a service entrance by the AHJ then the device must be "Service Entrance"rated.

You may have an instance where the upper device on the transformer secondary must be "Service Entrance" rated, but the lower device need not be.
If the device may be opened under load, then the device, whatever is used, must have an adequate ASSC rating, as well as adequate voltage and current ratings.
 
| don't think it is either an IEC or ANSI symbol. Looks more like a horn gap switch symbol, but that would not provide the protection needed.
 