shersan
Electrical
- Jun 17, 2002
- 11
Hello friends ,
There are total 6 Nos of 11kV , 3.2 MW cranes ( ship to shore ) to be fed from a 11kV substation. Total Connected load is equivalent is 19.2 MW . Maximum Loading for the incoming 11kV feeder is limited by the utility is 5.4 MW . To support 19.2 MW load ,then should have minimum of 4 Feeders . However one of our substation was running with 2 feeders for the same connected load wihtout any problem since 1 year . Our intention is to convince utility that we need only 2feeders ( or max of 3 ) instead of 4 feeders by saying the following .
1. Diversity of the crane itself is about 0.7 by knowing that the full load will not occur as this 3.2 MW consist of 4 individual operation motors which normally works only two at a time .
2. Second reason is that , it's very unlikely that the all 6 cranes will operate at full load at the same time . So the diversity applies ( approx .0.8 ) on the total connected load .
Any other resons ?????????????/
And why utility limited the one feeder ( 3c x 240 Sq mm XLPE , partly thrugh ducts and partly direct burieed , at a depth of 1 Meter down and soil resistivity is Middle east condition Etc ) is only 5.4 MW . No clues as by applying derating factor I'm getting about 7 MW .
By Giving more numbers of incoming feeders will constitute high cost and more switchgear , bigger size building .
Welcome some good suggestion to deal with this kind of issue .
There are total 6 Nos of 11kV , 3.2 MW cranes ( ship to shore ) to be fed from a 11kV substation. Total Connected load is equivalent is 19.2 MW . Maximum Loading for the incoming 11kV feeder is limited by the utility is 5.4 MW . To support 19.2 MW load ,then should have minimum of 4 Feeders . However one of our substation was running with 2 feeders for the same connected load wihtout any problem since 1 year . Our intention is to convince utility that we need only 2feeders ( or max of 3 ) instead of 4 feeders by saying the following .
1. Diversity of the crane itself is about 0.7 by knowing that the full load will not occur as this 3.2 MW consist of 4 individual operation motors which normally works only two at a time .
2. Second reason is that , it's very unlikely that the all 6 cranes will operate at full load at the same time . So the diversity applies ( approx .0.8 ) on the total connected load .
Any other resons ?????????????/
And why utility limited the one feeder ( 3c x 240 Sq mm XLPE , partly thrugh ducts and partly direct burieed , at a depth of 1 Meter down and soil resistivity is Middle east condition Etc ) is only 5.4 MW . No clues as by applying derating factor I'm getting about 7 MW .
By Giving more numbers of incoming feeders will constitute high cost and more switchgear , bigger size building .
Welcome some good suggestion to deal with this kind of issue .