Hello,
I've had a ground fault in my system for which an event recorder (SR750) is giving me ground currents that are not possible. This is a 6900V delta system with a 400A (10ohm) neutral grounding resistor. The phase and ground currents shown from the recorder are as follows:
A = 2810A
B = 3216A
C = 6854A
G = 1265A
I know that mathematically, the zero sequence current is 1285.69A. However, the maximum current possibly flowing through ground is 400A, as set by the NGR.
Has anyone run into this scenario before? I am assuming it is just a measurement anomaly, but unsure as to what is causing it, whether it be the CTs, the AC signal filters, the firmware, etc.
Any insight would be greatly appreciated.
Thank you.