clemsonCMT
Geotechnical
- Oct 16, 2007
- 4
I have searched the posts and have not seemed to find one similar to this so I will give it a shot. I have a client working on an existing hospital in SC. The hospital is being renovated and the existing grade adjacent to the basement walls needs to be raised approximately 5 feet. I am currently trying to figure out the increase in pressure along the face of the wall and what my options are for raising the grade. Removing the wall is not an option and reinforcing the wall further may not be either. Ineed to come up with a solution for raising the grade without increases the pressure on the wall. No design/specifics are available as to the construction of the basement wall. I figure if I do not increase the current condition then we would be safe.
The basement wall is 16 tall and backfilled with 11' of soil. I do not know the specifics on the soil type. I am assuming a combination of a clayey silt, silty clay being that those are the majority of the soils located here. The grade needs to be raised 5' in around this basement.
Doing some preliminary calculations I have used the at rest condition and solved the pressure per foot along the wall with Po=.5[ko(gamma ')H]H. Is my assumption right the wall is at an at rest condition. My calculations came to 3,620 #/ft for the existing condition with 11' of soil backfill.
Scenario 1: Raise the wall with soil assuming gamma' is 120 pcf. Po=7,680#/ft (No good)
Scenario 2: Remove the 11' of backfill soil and replace with 16' of 57 stone. Po=7,040. (No good)
Scenario 3: Remove 11' of backfill and replace with 16' of lightweight aggregate (SOLITE)
Po=4,800#/ft (No good)
Foam was also brought up but the cost seems way too high.
Any suggestions/alternatives would be greatly appreciated. I have not been on here long, but I really enjoy reading the posts and replys. Very imformative.
The basement wall is 16 tall and backfilled with 11' of soil. I do not know the specifics on the soil type. I am assuming a combination of a clayey silt, silty clay being that those are the majority of the soils located here. The grade needs to be raised 5' in around this basement.
Doing some preliminary calculations I have used the at rest condition and solved the pressure per foot along the wall with Po=.5[ko(gamma ')H]H. Is my assumption right the wall is at an at rest condition. My calculations came to 3,620 #/ft for the existing condition with 11' of soil backfill.
Scenario 1: Raise the wall with soil assuming gamma' is 120 pcf. Po=7,680#/ft (No good)
Scenario 2: Remove the 11' of backfill soil and replace with 16' of 57 stone. Po=7,040. (No good)
Scenario 3: Remove 11' of backfill and replace with 16' of lightweight aggregate (SOLITE)
Po=4,800#/ft (No good)
Foam was also brought up but the cost seems way too high.
Any suggestions/alternatives would be greatly appreciated. I have not been on here long, but I really enjoy reading the posts and replys. Very imformative.