A colleague has asked me to review his idea for increasing the permissible live load on an old (1950's era) flat plate slab supported on concrete columns with capitals, from the original design live load of 100 psf, to a new design live load of 250 psf for warehouse type loading. The building is 6 stories high and only the first suspended floor needs to have its live load increased in this manner. His proposal is to:
- place a reinforced bonded topping to act compositely with the old flat plate slab;
- add carbon fibre strip reinforcement on the bottom of the old slab (presumably fireproofed);
- add drilled-in grouted vertical reinforcement to increase the shear capacity.
He says he has checked the columns and footings and they work for the heavier loading.
Any comment?
- place a reinforced bonded topping to act compositely with the old flat plate slab;
- add carbon fibre strip reinforcement on the bottom of the old slab (presumably fireproofed);
- add drilled-in grouted vertical reinforcement to increase the shear capacity.
He says he has checked the columns and footings and they work for the heavier loading.
Any comment?