I am asked to provide input on the following project.
We have three 75HP 1800 rpm well water pumps. They pump into a common header, except that the tie-in points for the three pumps are widely separated (up to a mile apart I think).
The plant load varies widely. Up until now these machines have been fixed speed. Also the pumps are far from the operator’s stations so often the wrong number of pumps is running for the load (far to the left). We have had very low reliability. Presumably we are also wasting a lot in energy costs.
What has been proposed is to install VFD for each motor. Each motor will be controlled independently by sensing it’s discharge pressure and varying speed to match a target.
Also there is some kind of lead/lag feature where one pump would be designated to turn off during periods of extremely low load. There would be a time delay before the pump turned off and minimum off-time before it turns back on.
I am not very familiar with control schemes for this setup. I asked the question how do we control the load sharing and ensure the pumps are operating near BEP. I was told that all of the above parameters (pressure setpoints and time delays) will be adjustable. We will watch and see what it does and tweak as necessary.
The well water system is deemed relatively low priority to the plant and the project is expected low-budget and quick turnaround. We have quotes for the VFD system installed to feed existing motors at somewhere around $12,000 per pump. (Outdoor installation with cabinets).
My two questions:
1 – Is individual pressure control suitable for this type application?
2 – Is a detailed study of the system operating parameters required first, or is it ok to trust we can tweak it later.
3 – What do you think about the 3rd pump shutoff feature? I am worried that under certain conditions we are doomed to have constant cycling as soon as the time delays expire.
Thx.
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
We have three 75HP 1800 rpm well water pumps. They pump into a common header, except that the tie-in points for the three pumps are widely separated (up to a mile apart I think).
The plant load varies widely. Up until now these machines have been fixed speed. Also the pumps are far from the operator’s stations so often the wrong number of pumps is running for the load (far to the left). We have had very low reliability. Presumably we are also wasting a lot in energy costs.
What has been proposed is to install VFD for each motor. Each motor will be controlled independently by sensing it’s discharge pressure and varying speed to match a target.
Also there is some kind of lead/lag feature where one pump would be designated to turn off during periods of extremely low load. There would be a time delay before the pump turned off and minimum off-time before it turns back on.
I am not very familiar with control schemes for this setup. I asked the question how do we control the load sharing and ensure the pumps are operating near BEP. I was told that all of the above parameters (pressure setpoints and time delays) will be adjustable. We will watch and see what it does and tweak as necessary.
The well water system is deemed relatively low priority to the plant and the project is expected low-budget and quick turnaround. We have quotes for the VFD system installed to feed existing motors at somewhere around $12,000 per pump. (Outdoor installation with cabinets).
My two questions:
1 – Is individual pressure control suitable for this type application?
2 – Is a detailed study of the system operating parameters required first, or is it ok to trust we can tweak it later.
3 – What do you think about the 3rd pump shutoff feature? I am worried that under certain conditions we are doomed to have constant cycling as soon as the time delays expire.
Thx.
=====================================