Indicating Valves for Jockey Pump with ball valves

Status
Not open for further replies.

HnAw

Mining
Sep 10, 2013
3
0
0
PE
can Ball Valves work as indicating valves in suction and discharge lines for Jockey Pump?
 
Replies continue below

Recommended for you

NFPA 20-2013 4.25.5.2 Valves and components for the pressure maintenance pump shall not be required to be listed.

20-2013 4.25.5.7 The isolation valves serving the pressure maintenance pump shall not be required to be supervised.

It would appear ball valves are acceptable.
 