I am designing a restaurant's drainage system. I have a 3" floor sink which is receiving indirect drain(s) from the following equipment
Dripwell, Hand sink, Pasta Cooker and a scullery sink.
UPC Table 7-3 footnote 1 states that indirect waste receptors shall be sized based on the total drainage capacity of fixtures that drain therein to, in accordance with Table 7-4. This table gives GPM to DFU values.

Questions:
Do I have to calculate GPM drainage from every fixture? Or what if discharge GPM(s)for the fixtures are not known?

Please Help

Fayaz Din
 
Replies continue below

Recommended for you

The drain should be sized for all of the fixtures (4) it will drain. Use the table to determine the flow rate and pick a drain from a manufacturer's catalogue ie Wade, Josam.
 