Good morning folks,
Typically, when I design connections I check individual bolts for bearing and tearout capacity. On occasion, I'll end up with a single bolt failing in tearout while the summation of bolt bearing strength exceeds my requirement. For years, I've been making sure each individual bolt capacity exceeds the required strength but recently, I've been questioning whether this is too conservative.
For example:
AISC Table 10-1 shows that a beam web (coped at top flange w/ (3) 3/4" bolts) with an edge distance of 1-1/4" has an available strength of 133 kips/in (ASD).
If Lc = 1.25 - 0.8125/2,
Lower limit should be: (1.2*(1.25-0.8125/2)*(65ksi))/2.00 = 32.9 k/in for a single bolt in tearout
Upper limit should be: (2.4*3/4*(65ksi))/2 = 58.5 k/in
If Lc = 3-0.8125,
Lower limit should be: (1.2*(3-0.8125)*(65ksi))/2 = 85.3 k/in > 58.5 k/in
Therefore, assuming our beam web is 1" thick the total bearing strength is 149.9 kip.
But now what if the allowable reaction is 140 kip. Our bolt group exceeds the requirement but if we assume 140 kip/3 bolts -> 46.7 kip/bolt which is greater than 32.9 kip/bolt of tearout strength.
Do I assume that significant deformation has occurred at this bolt and now I only have 2 bolts resisting the reaction through bearing?
Would love to hear what you think.
Typically, when I design connections I check individual bolts for bearing and tearout capacity. On occasion, I'll end up with a single bolt failing in tearout while the summation of bolt bearing strength exceeds my requirement. For years, I've been making sure each individual bolt capacity exceeds the required strength but recently, I've been questioning whether this is too conservative.
For example:
AISC Table 10-1 shows that a beam web (coped at top flange w/ (3) 3/4" bolts) with an edge distance of 1-1/4" has an available strength of 133 kips/in (ASD).
If Lc = 1.25 - 0.8125/2,
Lower limit should be: (1.2*(1.25-0.8125/2)*(65ksi))/2.00 = 32.9 k/in for a single bolt in tearout
Upper limit should be: (2.4*3/4*(65ksi))/2 = 58.5 k/in
If Lc = 3-0.8125,
Lower limit should be: (1.2*(3-0.8125)*(65ksi))/2 = 85.3 k/in > 58.5 k/in
Therefore, assuming our beam web is 1" thick the total bearing strength is 149.9 kip.
But now what if the allowable reaction is 140 kip. Our bolt group exceeds the requirement but if we assume 140 kip/3 bolts -> 46.7 kip/bolt which is greater than 32.9 kip/bolt of tearout strength.
Do I assume that significant deformation has occurred at this bolt and now I only have 2 bolts resisting the reaction through bearing?
Would love to hear what you think.