pygmy_threat
Chemical
- Dec 11, 2018
- 2
I read a post about this from 2009. however, I am very weak in my electrical engineering...
I have a motor run indication to the DCS that is showing 65VAC when the wires (on both ends) are not connected to anything. the wires ohm out fine so no short. I definitely have induced voltage. I will use equipment names to help differentiate motors...
The DCS sends 24VDC through these wires to a switch in the motor contactor (Q1-801). When the contactor closes, the circuit is made and my DCS shows a run (Q-801). However, when a certain different motor (Q1-880B) runs, it causes induced voltage in my (q1-801) run indication wires and my DCS "sees" a closed circuit (it shows the motor to be running). We disconnected the run indication for Q1-801 from the motor contactor, we turned off the power, but Q1-801 still shows a run.
After reading the other post, it looks like 65VAC is a normal induced voltage. How do we trace where this induction is happening? Is it happening in the "home-run" bundle. I think it is a 16pair cable. Each pair is not shielded, but the entire bundle is shielded.
I think I understand from a previous thread that if you use un matched pairs, you increase the likelihood of inducing current. Is that true? why 65V? there must be some kind of calculation to figure out where this voltage is coming from....
if anyone has the old square"D" paper from the 2009 thread I would really appreciate a copy.
I have a motor run indication to the DCS that is showing 65VAC when the wires (on both ends) are not connected to anything. the wires ohm out fine so no short. I definitely have induced voltage. I will use equipment names to help differentiate motors...
The DCS sends 24VDC through these wires to a switch in the motor contactor (Q1-801). When the contactor closes, the circuit is made and my DCS shows a run (Q-801). However, when a certain different motor (Q1-880B) runs, it causes induced voltage in my (q1-801) run indication wires and my DCS "sees" a closed circuit (it shows the motor to be running). We disconnected the run indication for Q1-801 from the motor contactor, we turned off the power, but Q1-801 still shows a run.
After reading the other post, it looks like 65VAC is a normal induced voltage. How do we trace where this induction is happening? Is it happening in the "home-run" bundle. I think it is a 16pair cable. Each pair is not shielded, but the entire bundle is shielded.
I think I understand from a previous thread that if you use un matched pairs, you increase the likelihood of inducing current. Is that true? why 65V? there must be some kind of calculation to figure out where this voltage is coming from....
if anyone has the old square"D" paper from the 2009 thread I would really appreciate a copy.