I have a motor info as
HP 500 , kVA 450, poles 2, kV 4.16, Slip 1.275 RPM 3554, SF 1.15 , FLA 65
PF FL 100% -> 86%
Eff 100% -> 95
Locked Rotor:
%LRC 690%
%PF 19, T = 35% Tmax = 210

Can you please help me with equivalent circuit calculation and provide me with some references to go from these parameters to equivalent circuit?
 
Replies continue below

Recommended for you

Induction_motor_500_hp_3600_rpm_schematic_znogyy.jpg

I can calculate the parameters using my software-hand made on VB6-but I cannot send the
calculation only the results.
I hope it may be useful in a way. It is not possible to be close more than 5% because we have to neglect some of the losses as ferromagnetic losses, friction and ventilation.
For instance rated current will be 63.34A instead of 65A, pf=0.904 instead of 0.86.
 