aderemb
Electrical
- Mar 31, 2010
- 4
We have two induction motors that are connected to two seperate 4.16kV Medium Voltage Switchgear bus and both MV switchgears are fed from a single step-down main transformer. We experienced some problem with both of the induction motors stator winding temperature on phase "B" running at elevated level in relative to other two phases during the past summer.
We also observe that when any one of the motor in question is off-line, the stator winding temperature reading per phase is uniform across each phase. The difference only appears when either of the motor is running. This tell me that the sensors are calibrated correctly. The voltage and current per phase is not available in our DCS. However, we have few other induction motors connected on both MV switchgears that do not exhibit similar behavior across the stator windings when in service.
Motor Data: WEG Induction electric motor, 600HP, 80.7A rated current, 1188 RPM, 6 Poles, 4kV, 3Ø, 484A Lock-Rotor Current, 40°C design ambient temp.
Stator Winding RTD: Alarm at 130°C and trip at 155°C.
Question- Has any one experience similiar problem and how did you fix this problem. Any help will be highly appreciated.
We also observe that when any one of the motor in question is off-line, the stator winding temperature reading per phase is uniform across each phase. The difference only appears when either of the motor is running. This tell me that the sensors are calibrated correctly. The voltage and current per phase is not available in our DCS. However, we have few other induction motors connected on both MV switchgears that do not exhibit similar behavior across the stator windings when in service.
Motor Data: WEG Induction electric motor, 600HP, 80.7A rated current, 1188 RPM, 6 Poles, 4kV, 3Ø, 484A Lock-Rotor Current, 40°C design ambient temp.
Stator Winding RTD: Alarm at 130°C and trip at 155°C.
Question- Has any one experience similiar problem and how did you fix this problem. Any help will be highly appreciated.