In industrial equipment, we want to have the enclousre for the power and controls be a part of the equipment, instead of building or buying a speprate enclosure and mounting it in the equipment or on the equipment.

What regulations is the enclsoure requrieed to conform to for the USA and EU?

How can Idetermine if the enclsoure is "suitable" for use?
 
Replies continue below

Recommended for you

USA standards:
NFPA 79 "Electrical Standard for Industrial Machinery".
NFPA 70 Article 409 "Industrial Control Panels".
UL 508A "Industrial Control Panels".

EU standards:
CEI/IEC 60204-1 "Safety of Machinery-Electrical Equipment of Machines".




David Baird

Sr Controls Designer
EET degree.
Journeyman Electrician.
 