living2learn
Electrical
- Jan 7, 2010
- 142
I have an ingersoll rand 75hp, 480V air compressor. The utility that serves my site constanly has voltage drops that engage the critical fault 16 in my vfd. The problem with the critical fault is it requires a human to manually reset the system to restart, but a typical power outage does not require human interaction. The critical fault 16 is a DC undervoltage on the VFD. The ingersoll rand warranty is irrelevant, because this shutdown costs more than the compressor.
Porposed solution. Intercept the critical fault and route it to a relay that disconnects power to the unit - thus protecting it from a voltage sag. The relay will engage a 200A, 480V contactor that will isolate the compressor. Once power has been restored and my voltage sensing relay installed next to the contactor engages it will provide power to my air compressor.
Could I use a motor starter as the contactor?
What about a 200A lighting contactor?
Has anybody worked on these ingersoll rand compressors?
Thanks in advance for your input.
Porposed solution. Intercept the critical fault and route it to a relay that disconnects power to the unit - thus protecting it from a voltage sag. The relay will engage a 200A, 480V contactor that will isolate the compressor. Once power has been restored and my voltage sensing relay installed next to the contactor engages it will provide power to my air compressor.
Could I use a motor starter as the contactor?
What about a 200A lighting contactor?
Has anybody worked on these ingersoll rand compressors?
Thanks in advance for your input.