Inlet Plenums for AHUs

Status
Not open for further replies.

HVACHawaii

Mechanical
Feb 27, 2007
31
Anyone have any opinion on inlet plenums boxes? Are side connections to inlet plenums directly before filter boxes okay? I have a condition where we were not able to fit the ductwork otherwise, just wondering if anyone thinks this may be problematic. Any help is appreciated.
 
Replies continue below

Recommended for you

You may be short of air because you could have a condition known as stacking causing turbulance. Remember air flow in ducts resist changes in flow
 
You may also see uneven loading of the filters, which isn't a huge deal. Some may need changing before others.

If you're in Hawaii as your name suggests, you should have no concerns of freezing. if you are in a cold climate, the freeze stat may see well-mixed "warm" air while another part of the coil is seeing freezing air.

Otherwise, as long as you can get enough air, you may only be paying a penalty of a little more energy consumption.

 