sobeys81
Electrical
- Jul 13, 2008
- 63
Hi All,
I am sure that there might have been discussions about inrush current but I did not find any information relevant to my question.
I am trying to justify an information received from a manufacturer about inrush current calculation on a 1 MVA 13.8 kv transformer Dry type transformer. It talks a value of 6 to 8 times of full load current. The transformer is Delta/ Star Neutral grounded
As you know traditionally the concept of fuse selection for primary of transformer is to use 12X I(FL) for .1 sec and 25X I(FL) for .01 sec.
So how do I agree to the above value of 6 to 8 times inrush.
After talking to the manufacturer, I found out that while calculating the value of Inrush current theoritcally they
assume certain value of residual flux, which might lead the transformer in saturation for a short period of time and increase the inrush current.
Where in these calculations can we consider the impact of "Instand of Closing". Will that increase the value of inrush current and how does residual flux increase the inrush current.
Please refer me to any post that explains this concept or I would appreciate a word.
Thanks
I am sure that there might have been discussions about inrush current but I did not find any information relevant to my question.
I am trying to justify an information received from a manufacturer about inrush current calculation on a 1 MVA 13.8 kv transformer Dry type transformer. It talks a value of 6 to 8 times of full load current. The transformer is Delta/ Star Neutral grounded
As you know traditionally the concept of fuse selection for primary of transformer is to use 12X I(FL) for .1 sec and 25X I(FL) for .01 sec.
So how do I agree to the above value of 6 to 8 times inrush.
After talking to the manufacturer, I found out that while calculating the value of Inrush current theoritcally they
assume certain value of residual flux, which might lead the transformer in saturation for a short period of time and increase the inrush current.
Where in these calculations can we consider the impact of "Instand of Closing". Will that increase the value of inrush current and how does residual flux increase the inrush current.
Please refer me to any post that explains this concept or I would appreciate a word.
Thanks