Hey all,
The following redacted e-mail describes an issue we encountered within out utility when switching LV [28 kV & 44kV] capacitors:
<begins>
Hello!
Having witnessed arcing at cap enclosure padlocks and other equipment as well as CT failure, I can offer the following.
Anecdotal:
(1979) - a vague pattern of switching related failures developed when removing caps from service. A small group of ’78 OITs [operators in training] were requested to be at a specific transformer station when the next such operation was performed to observe any failure. When removing one of the ‘back-to-back’ capacitors, a CT exploded sending shrapnel across the switchyard. Over time, capacitor failures during ‘back-to-back’ switching had become such a concern that field staff would request any caps they were working close to not be in service.
The problem was thought to be caused when the removal of a 2nd cap from service would result in a surge from the 1st cap, spiking the voltage & causing untoward effects. This effect is of very short duration, viz., until the bus voltage settles to its new level. Adding the limiting reactor to the 1st Cap would reduce this spike to safer levels.
There is no similar problem when switching caps I/S, as switching the 2nd cap I/S would cause an MX spike into the 1st cap – not stressing all of the surrounding equipment.
Rule of thumb is: Reactor Equipped Cap is First In and Last Out - It’s the Last Out that is important.
Analogy: Looks like a spring to absorb the shock of switching the other cap...
<ends>
Incidentally, I don't think I've ever encountered a "large power factor cap bank" - they've all operated at almost zero, viz., very close to 90° leading...
![[bigsmile] [bigsmile] [bigsmile]](/data/assets/smilies/bigsmile.gif)
; they've only varied in voltage from, say 13.8 kV up to 240 kV, with ratings of between 10 and 410 MX; the higher voltage ones typically employ independent pole closing circuit breakers to mitigate that otherwise intensely nasty inrush current. Some of the 14 , 28 and 44 kV caps have current limiting reactors, and some don't, depending on local system configuration; our 115 and 230 kV caps have them almost without exception.