I apologize in advance for this rant.
If anyone has any pull or influence with the development of NFPA 13........
Please discuss the idiotic approach of installing Inspector's Test Connections at the sprinkler riser (12 in. downstream of the flow switch). This has been considered "acceptable" since 2002 and is quickly becoming standard practice. There are several serious reasons why this is a bad idea and from an engineering standpoint this is a very poor design. The inevitable trapped air in the system causes or can potentially cause a number of problems: Excessive system pressure when temperatures increase, false water flow alarms due to air pocket expansion/contraction, failed water flow alarms due to cycling flow switches, increased rust on the interior surfaces of sprinkler piping, etc.
From what I have seen, most contractors or sprinkler designers who primarily install or design new systems have no idea this approach causes problems for the building owner and/or fire protection system inspectors. I can confirm these are common problems at several of the facilities I have visited over the past few years. In many instances, the only effective solution is to install a suitable Inspector's Test Connection or bleed the air pockets using sprinklers at the highest elevations. The problem is access at some facilities after the solid ceilings or other obstructions have been introduced.
In my humble opinion, Inspector's Test Connections should be installed at the most remote point of each system. The connection point (prior to being piped to within 6 ft. of the floor level) should be at the highest elevation of the sprinkler system piping whenever possible. Auxilliary drains or low point drains should NOT be considered Inspector's Test Connections.
Just one man's perspective!! I wonder if anyone on this forum agrees with me on this subject.
If anyone has any pull or influence with the development of NFPA 13........
Please discuss the idiotic approach of installing Inspector's Test Connections at the sprinkler riser (12 in. downstream of the flow switch). This has been considered "acceptable" since 2002 and is quickly becoming standard practice. There are several serious reasons why this is a bad idea and from an engineering standpoint this is a very poor design. The inevitable trapped air in the system causes or can potentially cause a number of problems: Excessive system pressure when temperatures increase, false water flow alarms due to air pocket expansion/contraction, failed water flow alarms due to cycling flow switches, increased rust on the interior surfaces of sprinkler piping, etc.
From what I have seen, most contractors or sprinkler designers who primarily install or design new systems have no idea this approach causes problems for the building owner and/or fire protection system inspectors. I can confirm these are common problems at several of the facilities I have visited over the past few years. In many instances, the only effective solution is to install a suitable Inspector's Test Connection or bleed the air pockets using sprinklers at the highest elevations. The problem is access at some facilities after the solid ceilings or other obstructions have been introduced.
In my humble opinion, Inspector's Test Connections should be installed at the most remote point of each system. The connection point (prior to being piped to within 6 ft. of the floor level) should be at the highest elevation of the sprinkler system piping whenever possible. Auxilliary drains or low point drains should NOT be considered Inspector's Test Connections.
Just one man's perspective!! I wonder if anyone on this forum agrees with me on this subject.